Can anyone tell me why these voltage sine waves look odd?

Triple-n harmonics.Can anyone tell me why these voltage sine waves look odd?
Does the HVAC include a lot of VFD's?
It could be that the facility is not causing the problem and that it is actually on the incoming supply regardless of the loading at the facility.Does the HVAC include a lot of VFD's?
It could be that the facility is not causing the problem and that it is actually on the incoming supply regardless of the loading at the facility.
Third harmonic currents, if I remember back to university days, circulate in the delta winding.Good point. But if the facility has its own dedicated step down transformer, harmonics tend to cancel out in the primary (if its a delta).
(a) the supply impedance is low relative to the load being drawn.
(b) the supply voltage distortion is being imposed on the site and the cause of the distortion is external.
Clearly, in view of the above, compliance with spec. *** at the point of common coupling is not possible. The excessive level of supply voltage distortion being imposed should be brought to the attention of the supply authority.
The HV distortion will be reflected on the LV side of the transformer and this, together with the present 6-pulse load, means that the LV distortion will be close to the 6% limit which the customer wishes to meet. With the new loading which employs 12-pulse converters calculations indicate that the level of distortion will be similar.
Third harmonic currents, if I remember back to university days, circulate in the delta winding.
I'm not sure if the waveforms have anything to do with ballasts and blown hvac capacitors.
It could just be a case of a higher mortality rate from everything being new.
The flattened top results from typically third harmonic voltage. That means that there is a 180Hz component. Given that Xc = 1/ω the 180Hz component will increase the loading on the capacitors.120113-1950 EST
iwire:
If the nominal steady-state RMS AC line voltage is 120 V +/-10 V, then good quality well designed equipment should not fail as a result of the waveform distortion you are seeing.
.