Is there any code stating that when connecting a 25h.p air compressor you need to run flex from end of pipe to unit.I can understandif the unit is vibrating but it is setting on mounting pads and also has a e.g.c ran back to panel.Was informed that it is code to flex I've been checking book but not having any luck finding the art, pertaining to this. Thanks
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: flex from e.m.t

I do not think you will find an NEC requirement for flex in this location.

That said I would and always have used flex for this type of installation.

Is there a good reason not to use flex for the last foot or so? :confused:

There are good reason to use flex.
 

romeo

Senior Member
Re: flex from e.m.t

The only thing I could find was a commentary that it is a good practice to use flex on any motor. It should be less than 6ft. and contain a egc.

I agree with that comment.
 

marc deschenes

Senior Member
Re: flex from e.m.t

It is on mounting pads for a reason, if the mount should flex so should your wiring method. I would use the flex .
 