Yes that is what I was thinking, the distance is so short FMC might make more sense.You can use a non flexible raceway (i.e-EMT), a flexible raceway (i.e.- FMC) or a combination of both. At 2-4' I might opt for FMC only. Sometimes the spec limits the length. We've seen limits as short as 18" for the flex.
It's wall mounted? Why can you go directly into with non flexible metal raceway if floor mounted. I thought all xfrm's has to have flex out/in?Is the transformer floor mounted? If so you can go straight in with a non flexible raceway.
He might mean underground fed. Otherwise I agree, that good work practice is flex connection always. For the other part, it is generally about specs, and the company's vision on good workmanship. Most specs limit flex to 6'. OTOH, for a transformer 6' would be long and ugly in many people's opinion, but that also depends on how it is run. Generally anything more than 3 feet, I would likely transition to EMT.It's wall mounted? Why can you go directly into with non flexible metal raceway if floor mounted. I thought all xfrm's has to have flex out/in?
That is a design consideration.I thought all xfrm's has to have flex out/in?
Makes sense, thanks.He might mean underground fed. Otherwise I agree, that good work practice is flex connection always. For the other part, it is generally about specs, and the company's vision on good workmanship. Most specs limit flex to 6'. OTOH, for a transformer 6' would be long and ugly in many people's opinion, but that also depends on how it is run. Generally anything more than 3 feet, I would likely transition to EMT.
There is no requirement for flexible raceways for transformers. Some manufacturers recommend it to reduce noise, but do not require it. If you have loosened the frame hold down bolts, as required by the instructions, the use of flex does very little to reduce noise.I thought all xfrm's has to have flex out/in?
				