Interesting panel statement from the 2011 ROP:
Submitter: Ron L. Janikowski, City of Wausau, Wisconsin / Rep. CMP16
Special Editorial Task Group
Recommendation: Add new Exception to read as follows:
Exception to (5). Flexible cord as part of an assembly not exceeding 6 ft in
length shall be permitted above suspended or dropped ceilings, provided the
space above the ceiling is not in conflict with 300.22.
Substantiation: Security cameras, fire detection and other equipment that is
shipped with molded cord assemblies cannot be installed under current code
rules. I think short pieces of cord, part of a listed assembly should be allowed. I think a greater problem exists when the contractor tries to hand wire the equipment.
Panel Meeting Action: Reject
Panel Statement: The substantiation states that some equipment cannot be
installed under current code rules. There are currently provisions in the code
that address this issue and allow installation of cords above suspended ceilings.
The authority having jurisdiction could ultimately allow permission for these
types of installations based on 400.7(A)(3).
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11