deedubya
- louisville kentucky usa
Hello. New subscriber. First time posting.
My interpretations of NEC 400.10(A)(10), 400.12(6), and 501.140(A)(3) provide for use of flexible cords in conduit from a submersible pump (465 full load amps) to its power source (VFD). However, 400.12(2) says the cord can't run through "holes in walls...or floors". My submersible pump vendor supplies a German-manufactured flexible cord, (3) 120mm2 area (237MCM), stamped "SOW" on the jacket, 2 cords per pump.
My questions are:
1. Can I ignore 400.12(2)? This pump is in a Class I, Division 1 wet pit. It is unreasonable to expect that the VFD and the pump will be in the same space. There is no way to get a cord from the pump to its power source without going through "holes in walls or floors". I'm thinking 501.140(A)(3) waives this rule although it doesn't specifically say so.
2. Table 404.5(A)(1) only shows ampacities of flexible cords up to 2AWG for SOW cord. The vendor claims each cord is good for 344A per phase in conduit. 2 questions:
My questions are:
a. Is there any difference between ampacity in free air vs. in conduit? I was unable to find any difference.
b. Given the table only goes up to 2AWG, do I have to go through Neher-McGrath calcs in Annex B for larger conductors? My application has fairly large underground duct banks for part of the route. I have glance at the tables in Annex B and they only mention building wire insulations. And duct bank table ampacities I see in Table B.310.15(B)(2)(6) would indicate that ampacity of 237MCM is nowhere close to 344A.
It would be very clean and less expensive installation if I could extend these cords unbroken from pump to VFD. But my gut instinct is they are not sufficient per NEC. I don't trust myself to correctly calculate the ampacity of these cables and I don't trust that my vendor can either, or did. It will be a few hundred thousand $ in cord. I can't afford to be wrong. Thanks for your help.