True. But what about NEC 220.18 that requires 1.25% of motor full load current? 12A x 1.25 = 15A
This is one of those grey areas in the NEC. Even though the motor is UL listed, the cable is marginal to say the least and if you have any significant voltage drop you'll be in outright non-compliance. Personally I would have no issues with removing it and replacing it with the proper size.