Steelhead
Senior Member
- Location
- Southeastern Wisconsin
- Occupation
- Industrial Maint/Journeyman
When sizing flexible cord I'm not seeing anything in the code that states you need to size the cord at 125% of the FLA of the equipment you are attaching the cord and attachment plug to. We have several pieces of equipment in our plant that are connected with a cord and attachment plug where the cord is sized less than 125% of the nameplate FLA. I know that branch circuits for specific applications and applications where there is a continuous load that the conductors will need to be sized at 125%, but what about flexible cord?