I see that NEC allows FMC longer than 6ft as long as it’s not for a light fixture or motor, and that it has a ground conductor. Is this also true for hospital application?
Thanks for your prompt response. It would be for receptacles in offices for patient tracker monitors/tvs. So is it limited for that purpose?For wiring of receptacles in patient care areas the raceway must qualify as a 250.118 ground path so FMC would be limited to 6 ft for grounding purposes. It could be used outside of patient care areas and for luminaires in patient care that are above 7-1/2 ft above the floor.
YesAre they on the Critical branch?
Roger