AA5112
- Newnan,Ga. , United States
My lights flicker in my house until the a/c unit comes on and they stop. What could cause this? I had the power company check the service on the outside and they didn't find a problem.
When the lights were flickering last night I put my meter on a outlet on one of the outlets in the house and the voltage was jumping from 112-126 volts. When the a/c kicked on the lights stopped flickering and the voltage jumped to 130 volts and stopped flickering. I pulled the a/c breaker and inspected it. When I put it back voltage was 122v and the lights weren't flickering, but this morning it was starting again. I'm hoping maybe it's the breaker. It's got me pulling my hair out.
If you L-L is 240 and one side measures 130, you have a neutral connection issue somewhere.
Now if one side reads 130 the other should read 110, but you will have to be quick about changing leads or use two meters.L-L reads 240v
I checked voltage at the panel and have 115v on one leg and 126v on the other. I did notice a sizzling sound at the meter base. It sounds like it might have been coming from the disconnect there. Every neutral connection I have checked looks good and is tight. With the main disconnect open I read 120v on both legs on the meter side.