Never said what voltage AC runs at. Some have assumed it is 240 volt with 120 volt indoor blower - which is common but not necessarily what everybody has either.
That said I am still with others in that you are likely looking for a bad neutral connection someplace.
Most likely where the sizzling is !!!
Could be the meter jaws if it is a hot, or just a termination screw for the neutral which does not normally go to the meter itself.