The utility recently replaced a failing delta|delta 1000kva service entrance transformer in a commercial office building. The secondary is connected as a 3W+G system. There is no N-G bond and no ground fault detection.
250.20 Requires N-G bond where the system is 3-phase, 4-wire, wye connected in which the neutral conductor is used as a circuit conductor, however, the neutral is not used.
Since this is a wye secondary service entrance, wouldn't article 250.30 "Grounding Separately Derived Alternating-Current Systems" require a N-G bond?
Please help...we are concerned that this is a serious safety issue.