I recently came across something I was not able to figure out and only had a limited amount of time. I still may have to go back so I wanted to get some opinions. I got called to a mobile home because the occupants claimed power was out in a lot of rooms. When I got there, I found that phase to phase I had 240 V but from A to neutral I had 170 and from B to neutral I had about 70. When I shut everything off it balanced out with 120 on each phase to neutral. Then I turned the branch circuits on one at a time and each time the voltage was imbalanced. I would turn the breaker back off and the balance would return. When I was done, there were four single pole circuits that had to stay off in order for the voltage to stay balanced. Is this a loose neutral connection at the transformer that causes it not to get noticed until a load is put on the neutral? I was taking my measurements from the line side of the meter and I found out whatever condition existed. It existed from the indoor subpanel bus bar to the line side of the meter which is the last place I can get I’m reading from, but I felt that since the conditions were exactly the same between the bus bar and the line side of the meter the problem probably does not exist between those two points so it’s either on the branch circuits or ahead of the meter socket and I am hoping against hope that the problem is not somewhere inside the home. Does it make sense to think that it was one neutral connection at the transformer causing the issue?