Chris Philipp
Member
- Location
- Fairfax, IA

Well, I guess I'll try.
Why do they need to be "water tight"?
What is/are the code section(s) you failed it for? 406.9(D) Protection of floor receptacles?
406.5(F) Receptacles in seating areas & other similar surfaces?
I don't see a problem with mounting to the desk or the lower drawers opening. Inconvenient, yes. Violation, not that I know of.
Just trying to help.![]()
Yes failed for both of those and 314.27(B). Supports section 314.23 does not specifically spell out furniture as a support, but furniture is not structurally part of the building and could be picked up and moved at any time, with no consideration to the live circuit attached to the desk. My question is first, is my thinking reasonable on failing the original installation and second, would you agree that furniture is not adequate support by code definitions? Either way, thanks for the input as you can tell I'm a little unsure on the furniture as a support. It's great to have a forum like this to check other's code interpretations.
348.12 Uses Not Permitted. FMC shall not be used in the
following:
(1) In wet locations
(2) In hoistways, other than as permitted in 620.21(A)(1)
(3) In storage battery rooms
(4) In any hazardous (classified) location except as permitted
by other articles in this Code
(5) Where exposed to materials having a deteriorating effect
on the installed conductors, such as oil or gasoline
(6) Underground or embedded in poured concrete or aggregate
(7) Where subject to physical damage
Hard to tell from the pic but I don't see any connectors from that peice of flex to the 1900 box...
Well, I guess I'll try.
Why do they need to be "water tight"?
What is/are the code section(s) you failed it for?...
I don't see a problem with mounting to the desk or the lower drawers opening. Inconvenient, yes. Violation, not that I know of...
Yes 1900s are a 4 inch square box, I was told once where that name came from but it's slipping my mind right nowI'm assuming it's this kind:![]()
Never heard "1900 box" but I'm assuming that's what I learned as a "4-S box."
Yes 1900s are a 4 inch square box, I was told once where that name came from but it's slipping my mind right now
Sent from my SM-G950U using Tapatalk
That's right ty!!Old part number.
...the way the bottom drawers on the desk do not open, they hit the flexible conduit...