But what about it having to be readily accesible for inspection...no ladders etc.?
It does not have to be, please see what I have highlighted.
450.13 Accessibility. All transformers and transformer vaults shall be readily accessible to qualified personnel for inspection and maintenance or shall meet the requirements of 450.13(A) or 450.13(B).
(A) Open Installations. Dry-type transformers 600 volts, nominal, or less, located in the open on walls, columns, or structures, shall not be required to be readily accessible.
(B) Hollow Space Installations. Dry-type transformers 600 volts, nominal, or less and not exceeding 50 kVA shall be permitted in hollow spaces of buildings not permanently closed in by structure, provided they meet the ventilation requirements of 450.9 and separation from combustible ma-terials requirements of 450.21(A). Transformers so installed shall not be required to be readily accessible.
Notice it is readily accessible OR the others, IMO hanging from the ceiling is an open installation.