I haven't see that.

It makes no sense to use an intumescent caulk or pad on a metallic conduit. The reason for the use of an intumescent caulk is that it expands to fill the void left when a combustable material burns or melts away. I am not saying that there arn't any assemblies that use it, just that I haven't seen them.

Chris
Now you can say you have.... Any opening around any pentration be it PVC or RMC or anything in between (EMT) would need to be filled - with something. Often combinations of mineral wool, and intumesant puddy.
(for gaps around EMT)
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/wl/WL1175_020806.pdf
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/caj/CAJ0058_021406.pdf
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/caj/CAJ8107_042705.pdf

Not to confuse the OP, if the conduit is poured in place and does not have any gap - no fire-stop would be needed. That said many construction spec's in siezmic zones dont allow thru-penetrations to be poured in place due to movement - but that may not apply to his area, or by their buildings engineers.... Some others may require spacing of them.
 
Now you can say you have.... Any opening around any pentration be it PVC or RMC or anything in between (EMT) would need to be filled - with something. Often combinations of mineral wool, and intumesant puddy.
(for gaps around EMT)
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/wl/WL1175_020806.pdf
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/caj/CAJ0058_021406.pdf
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/caj/CAJ8107_042705.pdf

Not to confuse the OP, if the conduit is poured in place and does not have any gap - no fire-stop would be needed. That said many construction spec's in siezmic zones dont allow thru-penetrations to be poured in place due to movement - but that may not apply to his area, or by their buildings engineers.... Some others may require spacing of them.

Yes, now I can say that I have.;):)

There are many UL tested assemblys for thru-penetrations. These are utilizing a putty pad manufactured by Hilti, but there are literally hundreds of tested assemblies.

Chris
 
Yes, now I can say that I have.;):)

There are many UL tested assemblys for thru-penetrations. These are utilizing a putty pad manufactured by Hilti, but there are literally hundreds of tested assemblies.

Chris
TRUE - not looking to pick a bone wit cha - but I could find many more using intumescent - Really I have not come across many that dont use intumescent puddy, pads or sleeves of some nature or in combination with other stuff. One that I can think of that doesn't is 3M's mortar - which I have not used. I assume it has never seen it been spec'ed here due to it would crack and fall out if there were a quake. ;)
 
John and pierre I thought we covered this on post #6. I agree as well just the Annular space in a rated assembly would need fire blocked/stop/caulk. If the sleeves or EMT, etc, etc. are set and the deck is poured around the perimeter of the mentioned then it is a done deal.

Oh we did. I was just letting Pierre know that great minds think alike.:D

I could include you and Roger in there if you'ld like.:D:D
 