Now you can say you have.... Any opening around any pentration be it PVC or RMC or anything in between (EMT) would need to be filled - with something. Often combinations of mineral wool, and intumesant puddy.I haven't see that.
It makes no sense to use an intumescent caulk or pad on a metallic conduit. The reason for the use of an intumescent caulk is that it expands to fill the void left when a combustable material burns or melts away. I am not saying that there arn't any assemblies that use it, just that I haven't seen them.
Chris
(for gaps around EMT)
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/wl/WL1175_020806.pdf
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/caj/CAJ0058_021406.pdf
http://www.us.hilti.com/data/techlib/docs/ul firestop drawings/caj/CAJ8107_042705.pdf
Not to confuse the OP, if the conduit is poured in place and does not have any gap - no fire-stop would be needed. That said many construction spec's in siezmic zones dont allow thru-penetrations to be poured in place due to movement - but that may not apply to his area, or by their buildings engineers.... Some others may require spacing of them.