Just recently I had an E&I mechanic experience an electrical shock while reinstalling a fluorescent lighting fixture starter. The starter is a FS-4 30-40W. The mechanic was replacing the bulbs for the fixture, and noticed the starter seemed not to be installed correctly since the fixture did not illuminate once the bulbs were replaced. So the mechanic removed it, inspected the starter, and reinstalled it after noticing no damage. When he twisted the starter into place he felt an electrical shock, and described the sensation as "it lit me up". He was standing on a fiberglass ladder, and stated "that only his right hand touched the starter". When a voltage test was performed with a low voltage proximity tester on the starter and fixture, the tester did light up only in proximity of the starter not the fixture. When the starter was tested with a Tegam 110 voltage tester, the voltage measured was 5V to ground. There was several different grounds used to include the light fixture. The starter was removed and damage was noticed. During a continuity test between the starter's male terminals to its casing, one male terminal was shorted to the starter's casing. The starter was replaced, and the light fixture began operating. So my question is this since I'm not very familiar with fluorescent lighting starters, what is the voltage conducted through the starter? Is it the normal line voltage of 120V, or does it operate at a lower voltage? I am trying to understand why when tested, the voltage on the starter's casing was measured only at 5V, yet the mechanic stated he felt the shock enter his right side and exited his left while standing on a fiberglass ladder, i.e. note he also stated his left hand was touching nothing, not grounded. Is it due to the current of through the starter, or something else? Any help would be greatly appreciated. Also, the mechanic is fine and was released by medical personnel with no restrictions. Thanks