You need to study NFPA 497.
Read carefully, Divisions [Section 500.5] are defined in terms of possibilities not probabilities. "Classic" IEC Zones are defined in terms of probabilities; NEC Zones are somewhere in between to force-fit them (rather poorly IMO) to correspond to Divisions.
Technically, a Division 1 location may never have an ignitable concentration, it only has to be possible under "normal" operation. An example is the exhaust port of a pressure relief valve that never relieves - it's still Division 1 because if it ever did relieve, it was doing its job. (normal and common aren't synonymous)
The problem is normal isn't well undefined as it relates to hazardous location operations and Webster's 11th Collegiate Dictionary isn't too helpful either. For an interesting read, see Section 500.8(B)(5) as normal is applied motors.
Read carefully, Divisions [Section 500.5] are defined in terms of possibilities not probabilities. "Classic" IEC Zones are defined in terms of probabilities; NEC Zones are somewhere in between to force-fit them (rather poorly IMO) to correspond to Divisions.
Technically, a Division 1 location may never have an ignitable concentration, it only has to be possible under "normal" operation. An example is the exhaust port of a pressure relief valve that never relieves - it's still Division 1 because if it ever did relieve, it was doing its job. (normal and common aren't synonymous)
The problem is normal isn't well undefined as it relates to hazardous location operations and Webster's 11th Collegiate Dictionary isn't too helpful either. For an interesting read, see Section 500.8(B)(5) as normal is applied motors.