mikehughes8 said:As for as the Pearl Reconditioning standards go if you go to the web site listed in my previous post. At the bottom of many of their tables it says "Reproduced from NETA MTS – 1997 Table 10.14"
Fixed UBB Code
Table 10.14 is simply a temperature correction table for correcting your megger readings to 20 degrees C, has nothing to do with any testing procedures, and does not support your arguement at all. Tale 10.14 wasnt even derived by NETA, it is reproduced from the AVO publication "A stich in time".