fisherelectric
- Northern Va
I have a residential job that specs 4' and 2' single tube fluorescent fixtures w/ T8 tubes which are to be dimmed. The lighting designer says she will supply the fixtures but I will need to remove the original ballasts and lampholders and replace with dimming ballasts and rapid-start type lampholders and rewire the fixtures (unless she can find fixtures w/ rapid start lampholders). In addition the ballasts they will supply are for three lamps so I will have to wire three fixtures together on one ballast, I suppose by running flex between them. The dimmer is a 3wire electronic dimmer. The cut sheet notes that "Class 2 sensor wiring must be separated from all power and class 1 wiring..." and that the ballast has terminals for "power wiring, lamp wiring, and EcoSystem bus" in addition to a "class 2 sensor terminal". Does anyone know wether the third wire on this dimmer is class 2 or even what it's for. I believe the sensor terminal is for a different application.
The wiring diagram on the ballast cut sheet says "black (switched) hot, orange (dimmed hot), and neutral" plus the standard lamp wire terminals.
The specs also say the lamps must be "seasoned" for 12 hours before dimming, which I'm not sure what tjhat's about either.