Mr. Bill said:
I'm just curious why you think a single phase system wouldn't have harmonic currents.
[...] But there will always be some harmonics.
A single phase system might be able to cancel the harmonics on the neutral better when phase 'A' and 'B' are together.
A very good point.
If the load produces harmonics, then harmonics will be present. This is true for three phase systems, single phase systems, two phase systems, delta systems without a neutral, etc. These harmonics will be present on both the phase conductors and the neutral if loads are connected to the neutral.
The reason that we focus on the three phase neutral is that 'triplen' harmonics tend to be additive in this situation. In _most_ circumstances where harmonics may be present, they are simply additional load on the conductor. For example, in a single branch circuit (one hot, one neutral), harmonics may be present, and will be present in equal amounts on the two conductors. If there is lots of harmonic current, then this will show up as additional heating of the conductors, but no more than a similar RMS fundamental current (approximating to ignore skin effect, dielectric heating, etc).
In a single phase system, odd order harmonics will tend to cancel on the neutral, and so again are not a problem. The neutral acts the way that we've been trained, always having less current flow than the 'hots'. Harmonics may be present, but they don't generally cause unexpected loading. It is possible to come up with situations where harmonic currents will add on a single phase neutral, but to do so would require a contrived system, one that produces even order harmonics or which produces seriously strange and non-symmetric phase offsets for the harmonics on the two legs.
But in a three phase wye system, triplen harmonics tend to add. All the other current components cancel as expected, but in this system a subset of the harmonics _add_ on the neutral. This means that neutral loading will be greater than expected. If the harmonic content of the various load currents is high, then the neutral current (which is the _sum_ of currents from _three_ phase conductors) will be greater than the current on any of the individual phases. This is no stranger than the neutral current being less than the current on any of the individual phases, in the normal case where currents from the different phases cancel.
Summary: harmonics can be present on single phase systems and on the phase conductors of three phase systems...but they are particularly annoying when present on the neutral of a three phase wye system.
And this goes back to answering the original poster's question:
dSilanskas said:
Question is it true that the nutral carrys more on a fluorescent lighting load as opposed to in incandescent lighting load? and if so why?
Fluorescent ballasts _may_ produce harmonic current flows. If you have ballasts which produce harmonic current flows, and have a system where harmonic currents will add on the neutral, then the neutral current will be greater than expected. This is _not_ the case for a single phase system.
-Jon