Is there any prohibition against using the gutter space of a fluorescent strip fixture to pass extra conductors through, not associated with that lighting?
According to the UL Luminaire Marking Guide, luminaires listed for use as raceways are marked ``Suitable for Use as a Raceway'' and also ``Maximum of _____?C permitted in raceway.'' Without these markings, a row of luminaires connected end to end cannot be used as a raceway for circuit conductors other than the 2-wire or multiwire circuit supplying the luminaires. Luminaires identified for use as a raceway have been evaluated for the heat contribution caused by additional current-carrying conductors.
Are strip lights normally so marked? Or is this a rather rare, obscure fixture?roger said:Commentary from the Handbook;...
mdshunk said:Is there any prohibition against using the gutter space of a fluorescent strip fixture to pass extra conductors through, not associated with that lighting?
Thanks a million. I vaguely remembered that section, thus I asked my question. I'm still wondering if fixtures exist that are marked so that they can take additional conductors? It seems that with the newer electronic ballasts, there's tons of room to get by the ballast now.LarryFine said:Read 410.31, .32, and .33.
mdshunk said:Are strip lights normally so marked? Or is this a rather rare, obscure fixture?
Thanks. Just out of curiosity, do you use one brand, most normally? I know that myself, I sorta order them by the most generic description, and seem to get a different brand each time. Often, it's not all that clear to me exactly what brand the fixture actually is, even by reading the labels.roger said:Marc, actually most of the strip fixtures we use are listed as raceways.