dcspector said:410.28(E) but the intent is feeding through chain links.
Fluorescents don't work on DC.emahler said:sorry bob...i'm betting on dc...
iwire said:I don't see that section limited to that application.
In my opinion it also applies the conductors dropping down from the structure to chain hung strip lights.
FWIW in the 2008 it has moved to 410.56(E).
dcspector said:This is for let's say typical chain hung chandeliers, pendants, etc.with the manuf.cord and one would not try to feed solid conductors/cable thru the links...solid MC zip tied to a jack chain will not damage the cable and or conductors.
stickboy1375 said:But it really does not say that does it...
dcspector said:I This is for let's say typical chain hung chandeliers, pendants, etc.with the manuf.cord and one would not try to feed solid conductors/cable thru the links..
solid MC zip tied to a jack chain will not damage the cable and or conductors.
stickboy1375 said:But it really does not say that does it...
iwire said:I agree, but a chain hung fixture that could swing and flex the solid conductors could break the conductors.
dcspector said:Stick I agree with that but let's look at the (hate to say it) common sense or rationale on the installation. Solid MC running down along side a jack chain....so what! Now feeding it thru a fixture (luminaire) chain is a bit different, if even possible......Let's focus on the intent...damage to the cable and or conductors.
dcspector said:Let's focus on the intent...
iwire said:That would be one use of the section.
Keep in mind that the section is not limited to the chains but also 'movable or flexible parts'