Well let me learn somthin today a motor has a field and rotor basic simple 3 phase motor with vfd what your saying is increase the field magnatizing force beyond its needed torque normally and then dump this energy back to the dc buss does the dc buss need to lower its voltage or freq during this flux braking during a braking control time and place ? please explain to this oldman with just a limited electrical background with flux braking & control . How do we perform this and dont use a paddle fan in reverse i can flux brake one by holding the blades with my hand . Are we on the same page as a motor generator effect kinda ?
To answer Ohmhead's questions:
Yes, we are talking about operating the motor as a generator in order to stop the mechanical load. A generator requires mechanical power input to generate the electrical output. In the case of braking, that mechanical power input comes from the inertia of the load, and slows it down.
In order to achieve this 'dynamic braking', the VFD has to adjust its frequency, so that the rotor is spinning faster than the rotating magnetic field. This causes the motor to operate as a generator. The motor produces negative torque and slows the load down. The motor is also generating electricity.
The regenerated electricity has to go somewhere. With a normal VFD and normal regenerative braking, this electricity goes to charging up the DC bus. Very quickly, the voltage gets high enough that the drive trips on overvoltage (or the DC capacitors blow up).
The 'standard' method for dealing with this is to add a 'brake chopper' and 'braking resistor'; if the DC bus voltage gets high enough, then the brake chopper simply switches the resistor on to the DC bus. The resistor starts to discharge the bus, consuming some of this regenerated electricity. Another common method is to have a 'line regenerative' VFD, one capable of supplying power back to the AC mains. If the DC bus voltage gets high enough, then the VFD essentially becomes a grid tied inverter, and the regenerated electricity is used to supply other loads on the system.
What we have been talking about here are methods in which the regenerated electricity is used to heat the motor up, essentially by intentionally rendering the motor much less efficient. As you are aware, if a motor is operated at the wrong voltage, it becomes less efficient, meaning that it has greater losses (produces more heat) for the same output. The same is true when the motor is operated as a generator. If the machine is operated less efficiently, then for the same mechanical input, it produces less electrical output and heats up more.
In the case of 'flux braking' we are operating the motor as a generator, and additionally intentionally operating it as an _inefficient_ generator, so that the bulk of the mechanical input is converted to heat, with very little electrical output,
-Jon