My Question Is:
FM200 Is Required At Any Electrical Closet Including Cables According To Nec Or Not


Pls Advise
 
Thx Bob

So why it is highly recommended at Elec. Closet in the High rise buildings ( based on what )

Pls advise
 
I have never really worked a new high rise building so I can't comment on the building codes that may apply.

The only FM 200 systems I see installed are in data centers and important paper file rooms.

I have never seen an FM 200 installed in a run of the mill electrical room.
 
FM200 or any clean agent suppression like it (Inergen, Ecaro, etc) is not required by any nationally recognized code.
I design lots of electrical closets in NYC high rises and no clean agent suppression in the rooms.
 