I have a situation where the engineer spec'd 3.5" EMT with a short piece of FMC at the end of the run to feed a transformer. The conduit contains 5-#600 Kcmil conductors. According to the tables in annex C, 3.5" EMT is permitted to contain 5-#600 conductors, the FMC is only permitted to contain 4-#600 conductors. But since the FMC is less than 24" in length the fill increases to 60% which now allows the 5-#600's.
My question is about the 90 degree 3.5" FMC angle connector, how would you know if the connector is listed for the 5-600's? The 5-600's are permitted in the EMT, and within the FMC nipple but what about the connector? I've never seen an FMC connector that listed the size and number of conductors permitted within them.
My question is about the 90 degree 3.5" FMC angle connector, how would you know if the connector is listed for the 5-600's? The 5-600's are permitted in the EMT, and within the FMC nipple but what about the connector? I've never seen an FMC connector that listed the size and number of conductors permitted within them.