FMC installed into a PB

Status
Not open for further replies.

seabeece2

New member
Is there any stipulation in the Code on installing Flex Metal Conduit into a Panel as a homerun in an Industrial/Commercial setting?
I searced Art, 350 and couldn't find a thing yet my Sup. tells me it is a violation. Thank You!
 

peter d

Senior Member
Location
New England
Re: FMC installed into a PB

yet my Sup. tells me it is a violation
He/she is wrong. There are no restrictions as long as the provisions of the article are met.

Flexible Metal Conduit is article 348, not 350.

[ December 02, 2004, 12:51 AM: Message edited by: peter d ]
 

seabeece

Member
Re: FMC installed into a PB

Flexible Metal Conduit is article 348, not 350. [/QB][/QUOTE]

Been looking at an older NEC where it is Art 350. Thanks for your help
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: FMC installed into a PB

Many industrial specs prohibit runs of flexible conduit of any type other than at terminations of motors and other devices that vibrate. usually this is limited to 6 feet.

It may not be a NEC violation but could well violate the plant specs.
 