Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
I often see FMC from xfrmr to panel unsupported, granted it's only a few feet. What's the distance limitations for supporting FMC? Thanks
Thank you.348.30
Ron
I would give them a green tag.So as far as I can see none of these FMC whips are supported. Does this fall under 348.30(a) exception 2?
View attachment 2569225
What do you mean?I would give them a green tag.
Ron
Not sure what you mean by the xfrm side? A panel FEEDS the xfrmr and a panel is being FED by the xfrmr.I agree with Ron yes it would pass that way but I would expect there to be 1 strap for the support on the panel side then the exception would apply for the transformer side being unsupported for the short distance.
Yes agree too. 334.30 requires "FMC shall be securely fastened in place by an approved means within 300 mm (12 in.) of each box, cabinet, conduit body, or other conduit termination and shall be supported and secured at intervals...." So it should have at least the one strap at panel side per exception:I agree with Ron yes it would pass that way but I would expect there to be 1 strap for the support on the panel side then the exception would apply for the transformer side being unsupported for the short distance.
I wondered that too. Anything about a transformer enclosure that would prohibit attaching to it? I don't know. Doing mostly residential don't get much into the transformers of this type.Why can't it be secured to the transformer with a minerlac or a piece of strut on the transformer with a strut clamp?
Do transformers generally have vibration isolators, and if so are they internal to the case (isolating the transformer from the enclosure) or external to the case? If the latter, then arguably "flexibility is necessary after installation" for the vibration isolators to work as intended.While the examples in the photos aren't egregious, in my opinion the exception does not apply.
There are some that have isolation built in between the core and case within the transformer. They usually require the installer to back off the nuts on the mounting bolts to allow the core to "float". More often the vibration elimination is done externally with springs or pads under the transformer frame.Do transformers generally have vibration isolators, and if so are they internal to the case (isolating the transformer from the enclosure) or external to the case? If the latter, then arguably "flexibility is necessary after installation" for the vibration isolators to work as intended.
Cheers, Wayne
Why does so many think you need flex here. I would have ran the EMT all the way to the transformer if I were doing the install pictured here. Nothing wrong with entering near the back either if you don't want the extra bend in the raceway Plenty of room for the conductors below the support for the coils, but if entering near the front you could always use a conduit body for the short turn.Nothing would prohibit it and it helps to keep the angle connector from turning.
View attachment 2569245
Again, if the enclosure is on external vibration pads/springs, flexibility is required. Hard piping to the enclosure will restrain it from movement and become the predominant conveyor of vibrations.Why does so many think you need flex here. I would have ran the EMT all the way to the transformer if I were doing the install pictured here.