We might load shed the owners oven, or air conditioner. To be determined. So yes it will carry the load of the house.
Hey iwire.
We might load shed the owners oven, or air conditioner. To be determined. So yes it will carry the load of the house.
Hey guys any more thoughts.We might load shed the owners oven, or air conditioner. To be determined. So yes it will carry the load of the house.
See post 14.
I don't see where OP says one way or the other.
You think 20KW is a whole home generator?
You think the inspector is unaware of the reduced feeder sizes in dwelling units?
How about we wait for the OP to respond before going out in the weeds.
Hey iwire.
Sticking with NEC terms, it still is not a service, but is the only source at that time, but if it transfers only to selected circuits it doesn't have the same load diversity as if it were capable of supplying the entire dwelling load - which is why 310.15(B)(7) exists in the first place, the entire dwelling load has a different load diversity then selected portions of it. NEC doesn't let us determine for ourselves what the load diversity might be though.Since the Gen is the only service when the transfer switch is thrown and any other loads are shed it's a no brainer it carries the entire load of the dwelling as it is now a service.
Sticking with NEC terms, it still is not a service, but is the only source at that time, but if it transfers only to selected circuits it doesn't have the same load diversity as if it were capable of supplying the entire dwelling load - which is why 310.15(B)(7) exists in the first place, the entire dwelling load has a different load diversity then selected portions of it. NEC doesn't let us determine for ourselves what the load diversity might be though.
702.4 requires a load calculation.This is a tad confusing. I see nothing in 445 or 705 that requires a demand load calculation for a genny install, although some insist a 'whole house T switch' would qualify as just that, with the 'wrench' of load shed salted in the wound...
So perhaps a pertinent Q would be in design? ...., would there be a difference in placing said T switch before vs. after the main(s) ,ergo it is or is not technically service equipment?
like>>>
![]()
~RJ~
That hits the nail on the head IMO. Taken to the extreme, suppose we shed all but one load, then it should be clear an "over-amped" conductor would not be appropriate.Sticking with NEC terms, it still is not a service, but is the only source at that time, but if it transfers only to selected circuits it doesn't have the same load diversity as if it were capable of supplying the entire dwelling load - which is why 310.15(B)(7) exists in the first place, the entire dwelling load has a different load diversity then selected portions of it. NEC doesn't let us determine for ourselves what the load diversity might be though.
You think 20KW is a whole home generator?
You think the inspector is unaware of the reduced feeder sizes in dwelling units?
How about we wait for the OP to respond before going out in the weeds.
Since the Gen is the only service when the transfer switch is thrown and any other loads are shed it's a no brainer it carries the entire load of the dwelling as it is now a service.
Sticking with NEC terms, it still is not a service, but is the only source at that time, but if it transfers only to selected circuits it doesn't have the same load diversity as if it were capable of supplying the entire dwelling load - which is why 310.15(B)(7) exists in the first place, the entire dwelling load has a different load diversity then selected portions of it. NEC doesn't let us determine for ourselves what the load diversity might be though.
Nope. You are using common sense instead of applying the NEC.
702.4 requires a load calculation.
We might load shed the owners oven, or air conditioner. To be determined. So yes it will carry the load of the house.
Hey iwire.
Would #4cu be mfg spec'd because the generator wouldnt be run above 80% capacity? otoh, why not run #3 and be covered? If you can physically install #2 AL, #3 Cu will fit the lugs/terminals... and #1AL would be cheaper, if it will fit.
Yes I am aware of this now. Made a error. The #2 al is in the 100 ser we ran through basement.
Looking to understand if we can find a way around this without pulling new. Manufacturer does not support changing breaker. So..... idk
sorry I wire do not have a solid answer on load calc. Customer purchased gen set up, I'm helping install.
At this point should have trusted my gut and said no thanks. But I'm in it now. I'll see it through.
Sort of been my thought all through this process. Probably cost less then the unit mount breaker in the generator anyway.What about a 90A breaker/fused disco between the generator and panel?