Single set of 500 kcmil CU from 4000 amp main switchboard exceeding 25' to 400 amp fusible safety switch (FSS) fused at 400 amps.
Load of FSS is parallel 250 kcmil CU to trough
from trough parallel 350 kcmil Al to Normal connections in 600 amp ATS
Single set of 500 kcmil CU from load connections in ATS to trough where it is connected to single set of 4/0 CU.
The 4/0 goes to a line connections of a 400 amp FSS fused at 250 amps.
From here a single set of 350 kcmil AL go to a single elevator 61 amps FLA
additionally a single set of 350 kcmil AL goes 18 floors to a 400 amp MLO panel with elevator lighting loads and 2 - 61 FLA elevators and 4 - 49 FLA elevators.
And they wonder why the conduit is warm (HOT).