- Chapel Hill, NC
- Retired Electrical Contractor
I have a similar issue also. I wrote a proposal for art. 338 and I am not sure they read thru it or perhaps I am missing something. Would someone read it and tell me if I am off base. 338.10(B) states that USE as a feeder or branch circuit must follow part II of art. 340. Art. 340.80 states that uf must be rated 60C. This means to me that USE must be 60C as a feeder-- I don't think that is the intent and I see they agree but I don't understand their response about single conductor without a jacket
7-59 Log #817 NEC-P07 Final Action: Reject
(338.10(B)(4)(b))
________________________________________________________________
Submitter: Dennis Alwon, Alwon Electric Inc.
Recommendation: Revise text to read as follows:
(b) Exterior Installations. In addition to the provisions of this article, service entrance cable used for feeders or branch circuits, where installed as exterior wiring, shall be installed in accordance with Part I of Article 225. The cable shall be supported in accordance with 334.30. Type USE cable installed as underground feeder and branch circuit cable shall comply with Part II of Article 340, excluding 340.80
Substantiation: Why should USE cable be subject to the 60C ampacity rating of UF, NM and SEU and only as a feeder or branch circuit. I thought the concept for the 60C rating is because of insulation around a cable. When USE enters a building, if it is dual rated, then it must be in conduit so why would a cable rated 90C in dry location now be subject to 60C rating. Also underground it is rated 75C but now it must be limited to 60C when used as a feeder or branch circuit. I believe this was an oversight but I may be incorrect. It won?t be the first time.
Panel Meeting Action: Reject
Panel Statement: The submitter is referring to single conductor USE per Table 310.104(A), whereas 338.10(B)(4)(b) is referring to a USE cable assembly with a plastic covering as defined in 338.2. Single conductor USE is not limited to the ampacity in 340.80.
Number Eligible to Vote: 14