I ran a 225amp feed 400ft with (2) 2?conduits - 4 #2/0 THHN copper each, to a 225 amp dock powered pedestal. To prevent an extreme voltage drop I up sized my wire and ran parallel runs. The problem is that I have installed my OCPD in line prier of going down to the dock , and now, I am finding out that the 225A circuit breaker within the Disconnect will not accept two 2/0 wires or double lugs. So, what I?ve done is, I?ve cut in a junction box to tap and extend each conductor, both line and load with a single 4/0 wire going too and from the circuit breaker. This connection is made using a ?Greave? connector rated for 250kcmil to a # 6 AWG.
This is what the inspector needs to see the torque on as well as the circuit breaker,
Oh, the main 225A circuit breaker won?t accept the two wire?s as well.