augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 14, 2010 #1 I have a cable tray with two barriers. One section has power, one data, and the third process piping for fluids. In reviewing Art 392 I don;t find where this is prohibited. Is this a Code violation ?
I have a cable tray with two barriers. One section has power, one data, and the third process piping for fluids. In reviewing Art 392 I don;t find where this is prohibited. Is this a Code violation ?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 14, 2010 #3 missed that THANKS
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Jun 14, 2010 #4 I think an argument can be made on this one. For practical purposes, the barriers create 3 separate raceways. If there are no conductors mixed in with the process piping, it might fly. Its not real uncommon to route air control lines this way. However, I think there is also a requirement that raceways not be used to support other equipment that is harder to get past. Last edited: Jun 14, 2010
I think an argument can be made on this one. For practical purposes, the barriers create 3 separate raceways. If there are no conductors mixed in with the process piping, it might fly. Its not real uncommon to route air control lines this way. However, I think there is also a requirement that raceways not be used to support other equipment that is harder to get past.