Please reword or explain in different ways... perhaps more detail. As worded, your questions do not make any sense regarding the subject matter.Do we have execusions for this artilcle. Also i need to know what is the range of transformer vault.
Ok, Can we run the water pipes in transformer room.Please reword or explain in different ways... perhaps more detail. As worded, your questions do not make any sense regarding the subject matter.
If by transformer room you mean transformer vault, water pipes that do not deliver water specifically to the vault for a related purpose are not permitted... and I can't imagine water needing delivered to a transformer vault. Uncertain what you mean by "range" and "avoid", but IMO the preceding is true for the entire vault "cavity".Ok, Can we run the water pipes in transformer room.
If yes, what is the range of transformer vault to avoid that.
Fire protection piping and chilled water for air handlers designed to keep the transformers cool are allowed. All others are not.
According to our local inspectors, only the chilled water branch that serves the air handler in that room is allowed.