JamesBonded
Member
- Location
- New York, NY
I'm hoping someone on this forum can give me some insight into what exactly happened during a recent screwup by an electrician I have working for me. The situation is as follows - I recently had an electrician install a regular 120V 1P duplex outlet in a large room in the basement of a new building that is in the construction phase. The building has a 120/208 3P service. When he was wiring the outlet, he had run out of white conductor for the neutral, so he used a red conductor instead, but wrapped it in white electrical tape at the outlet. He also used a red conductor for the hot leg. Unfortunately, his assistant who was connecting the outlet to the circuit back at the panel didn't get the memo, and connected the first red wire to a single phase circuit and connected the other red wire (not wrapped in white tape at the panel, only at the outlet) to another circuit on the same phase as the first red conductor. So, fast forward an hour and we go to plug in a simple 120V dehumidifier to the outlet. The dehumidifier runs initially, but then burns out after about 30min of operation. So, my question is this - Did the dehumidifier burn out because this wiring configuration (2 red conductors and a ground) brought 208V to the dehumidifier or 240V to the dehumidifier? If someone has any insight into what actually happened here, I'd love to know.