Code requires largest motor load be included in the summing at 125%. Whether you do it separately or just add the 25% separately is user's choice. The main issue is that the plans examiner or inspector be able to realize which way you did it...Regarding to the the total computation of load of line current.
Do I need to separate the highest motor rating current when I'm applying the demand factor or it must be combined on the demand factor in order to size correctly the breaker of the panel. thanks guys.
Starting current is not part of the service or feeder calculation. The reason for the extra 25% of the largest motor is not to provide for starting current. It is to cover the possibility of continuous and full loading of all the motors. Since it is only a possibility that all motors will be run continuously, and at full load, and more likely they will not, the extra 25% of the largest should cover the demand if it should ever be at its maximum. Perhaps not as stringent as 125% for all continuous loads, but historical evidence has shown the requirement, as is, to suffice in practically all scenarios.yes, i think that is also one of the issue, but there's a difference in the total line current that's why I want to clear whether the starting current of the motor which is the 25% must be also be in the demand factor, specially when the load schedule is are mixed of single and three phase loads. thank you.
Thank you so much for the information.. Can I ask the formula you using for this topic? I just need some reference and comparisons. Thank you.![]()
:grin: im asking for the formula you using for finding the total line current of a panel in order to size the main breaker panel and to give the correct wire size to be used, of course there's no formula for the finding the highest motor rating, i know that.. hehe! thanx.
I see you are wise beyond your earsok, i will just look up and read the article.
For single phase line to neutral it is rather obvious the VA load is assigned entirely to its connected line. Three phase loads (balanced) you assign one third of the load VA to each line. For single phase, line-to-line, you assign one-half the load VA to each connected line.You are right, Im also concern on the method you used if the load is a combination of three phase and single phase.
This method slightly flawed, but if the system is reasonably balanced out, it suffices... besides, engineers have been doing it this way without a problem since before I was born. No sense in breaking with tradition![]()
If I recall correctly, yes. But I've never been one to recognize "o.f.f." as anything meaningful. It is just an peculiarity of the calculations.Is the flaw you are referring to what is called the oregon fudge factor and due to the fact that there is a 120deg phase shift between currents in a 3 phase system?