formula
I would like to know the formula to figure out wire size and overcurrent size for a particular situation. 460 volt 3 phase bus duct feeding a 64 kva piece of machinery.
Re: formula
Do you have a code book?
If its a motor follow the rules for ampacity of conductors in Art 430. Conductors are sized per Table 310.16.
Or are you asking how to convert 64 kva into a ampere load?
Re: formula
I would be happy to help you for a fee of 110 dollars an hour for the calcs...
just kidding... :)
Lady :)
Re: formula
As already asked, what specifically is the equipment? It should have a nameplate & on that nameplate is an ampere rating. According to code this information is what you need to use.
[ January 21, 2004, 06:35 PM: Message edited by: ctrider ]