allenwayne
Senior Member
It is my understanding that a concrete encased electrode can only be spliced with a non reversible means IE: cad weld or approved crimp or irreversible split bolt ( I have not found these)
We are now required to use this ground system and last week I had calls from 2 rough crews thet the wire had been cut off. Both about 1 ft out of footer With production as it is I scrambled and found a crimp sleeve listed for #4 doesn`t say solid or stranded
Just #4 CU so using a crimp tool we added the length we needed.Yesterday the AHJ said why dont you sink a ground rod snd scorn it and use a 2 nd piece of ground wire under a 2 nd acorn to make connection
Acorns are not irreversible unless we alter them with a hack saw.