Four conductors

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
I will be installing an outdoor panel in the coming weeks. This a Bar and grill and there are already two services. They both come from a tie box under meter or should I say meter feeds bus bar and these two services attach to bus. Now I need to run another service from this bus , does it have to have four wires or do I just three and install ground bar that new service panel. So there will three independent services coming from this same bus. Power company is alright tiring in to bus but do I run 4 wires or 3.
 
I will be installing an outdoor panel in the coming weeks. This a Bar and grill and there are already two services. They both come from a tie box under meter or should I say meter feeds bus bar and these two services attach to bus. Now I need to run another service from this bus , does it have to have four wires or do I just three and install ground bar that new service panel. So there will three independent services coming from this same bus. Power company is alright tiring in to bus but do I run 4 wires or 3.
Where is your service disconnect? Do you have one, or by the sounds of it, you have three.

Grouped together,of course.
 
One service, two or three feeders.

An EGC is a must, so are you asking about omitting the neutral or one line?
 
If the conductors you are adding are service conductors and this is a single-phase service, 3 conductors (with a bonded neutral in your panel).
If there is a service disconnect ahead of the panel you are adding then the conductors are feeders and a EGC would need to be added.
 
Yes Augie these are all service conductors , single-phase. There is no disconnect before them. Thank you
 