Senior Member
- Location
- Massachusetts
I need to run four three phase 48- volt circuits from the top (18th) floor of a high-rise building up through the elevator machine room and up through the roof of the machine room. With the help of some folks here I have learned that I can't run through the elevator machine room but it is virtually the only way to get to the roof where I need to feed four draft fan motors. The fans will be fed and controlled by four VFD's. I also learned here that running the four VFD outputs in one conduit is a bad idea.
Today I found what I hope is a good solution. There is a 3" conduit that runs from the 18th floor to the roof. The conduit is about 15 feet long. Would the code allow me to use the conduit as a sleeve? I believe the four cables would easily fit. I would be running four 10-3 jacketed MC cables. The motors are 15HP. The contract calls for the conductors to be #10.
Would derating be an issue with 12 CCC's?
I would run the four cables to a junction box on the roof. Would splicing the conductors in the box be an issue? Code wise I think not. I would run from the box on the roof to each fan disconnect using thhn/thwn in individual conduits. Would having the VFD outputs spliced in the same box be a problem or am I trying to keep all them all shielded from each other?
If the VFD outputs must remain shielded from each other I could continue the MC run all the way to the fan disconnect.
Today I found what I hope is a good solution. There is a 3" conduit that runs from the 18th floor to the roof. The conduit is about 15 feet long. Would the code allow me to use the conduit as a sleeve? I believe the four cables would easily fit. I would be running four 10-3 jacketed MC cables. The motors are 15HP. The contract calls for the conductors to be #10.
Would derating be an issue with 12 CCC's?
I would run the four cables to a junction box on the roof. Would splicing the conductors in the box be an issue? Code wise I think not. I would run from the box on the roof to each fan disconnect using thhn/thwn in individual conduits. Would having the VFD outputs spliced in the same box be a problem or am I trying to keep all them all shielded from each other?
If the VFD outputs must remain shielded from each other I could continue the MC run all the way to the fan disconnect.