mkgrady
Senior Member
- Location
- Massachusetts
[310.15(B)(3)(a)(4)(a)] You would need unjacketed #12 to not have to derate....
[330.10(A)(11)] but you need jacketed in the 16" above the roof to qualify for the wet location usage...
...so you use jacketed and strip off the jacket for all but the 16" above the roof, and
[310.15(A)(2) Exception] use the adjacent rule to not have to derate that 16".
I think I will use the 10-3 jacketed, strip the last 16" of jacket and see what happens. It just seems stupid to have to use #8 where #12 wire would be large enough. I'm picturing a discussion with the inspector as follows:
Inspector. You used #10 wires and therefore they must be derated. Put in #8.
Me. How about I install #12 instead?
Inspector. OK that will work