S sbrown New member Aug 23, 2005 #1 I've installed a FPE 150amp breaker rated at 40c.The feeder size is 1/0 thhn copper is this to code. Article 310-16 states that 1/0 cu is rated at 150amps using the 75c chart.By this breaker having 40c issuance will it still work. thanks :roll:
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 23, 2005 #2 Re: FPE Breaker sounds like a trick question...where does one find a FPE breaker.. I believe 110-14(c) would prohibit the 1/0.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Aug 23, 2005 #3 Re: FPE Breaker Sounds fine to me. The 40 degree Celsius rating is for the ambient temperature of the breaker not the conductor temperature.