mstrlucky74

Senior Member
Location
NJ
Curious as to what cable you guys would use for the class 2 between power packs and from packs to sensors if running above hung ceiling. Thanks.
 

Attachments

  • Capture.JPG
    Capture.JPG
    38 KB · Views: 0
I assume "free air" means not in raceways. If space above ceiling is used for environmental air handling, you need to use plenum rated cable.
 
I assume "free air" means not in raceways. If space above ceiling is used for environmental air handling, you need to use plenum rated cable.

Yes, I know. Just curious as to what guys runs in this situation....a Belden type cable is what I think. Thanks.
 
If it is for a class 2 circuit a CL2 rated cable is acceptable, and plenum rated if in an air handling space, but nothing says you can't run RMC with THHN/THWN or MC cable either, but the CL2 cable probably cost less and is likely less labor to install as well.
 