Free Air or not

Status
Not open for further replies.

btharmy

Senior Member
Location
Indiana
in a distrubution panel

You answered your own question. If it is '"in a distribution panel" then it can not at the same time be in free air. Free air implies the cable can dissipate heat better because it is not enclosed in anything that will contain the heat generated. I suppose if the cabinet is ventilated with fan forced air, and can be proven to not retain the heat genrated by current carrying conductors, you might have an argument. But if it is in a distribution cabinet, one can only imagine the heat generated by all the other conductors and overcurrent devices in the same cabinet would override the effect of ventilation.
 