brian john
Senior Member
- Location
- Kilmarnock, Va
- Occupation
- Retired after 52 years in the trade.
Ran into an unusual problem, I have a 100 KVA Liebert DataWave feeding 3 phase power supplies to some blade servers, AT 38% load no real issues (noisier that I would expect but sounds like 60 HZ. Above 38% load and the unit sounds like an air compressor. Performed a resistive load test on the unit and no issues at any load percentages. Run the blades above 38% with load bank on line and no issues shut off load bank and the compressor sound starts up.
38 % Load
		
		
	
	
		 
	
Above 38% load bank is not on line at this point.
		 
	
Frequency
		 
	
Voltage THD Harmonics were primarily 5, 7, 11, 13 assuming 6 pulse rectifier?
		 
	
	
		
			
		
		
	
				
			38 % Load
 
	Above 38% load bank is not on line at this point.
 
	Frequency
 
	Voltage THD Harmonics were primarily 5, 7, 11, 13 assuming 6 pulse rectifier?
 
	 
				
 
 
		