Physics,
Don
My understanding is that everything in the interconnect is at the same frequency. The generators that are connected together act as one very large machine. Once they are tied to the grid their frequency is locked to that of the grid. Large increases in load serve to drive the frequency down a bit. At this point the frequency controls (governors) will increase the mechanical power input to the generators to drive the frequency back up. Since the grid has no real method of storing electricity the generation must always be matched exactly to the load. When it is not, there will be small changes in frequency to bring everything back into balance. That is when the load exceeds the generation the frequency drops and when the generator exceeds the load the frequency increases.That's something that's always interested me Don, not enough to actually try to find out I suppose, but what in the world is the method used to keep all these individual generators, or alternators, in synch?
Don