Fridays Failure Forum Picture for Mar. 23 2007

Status
Not open for further replies.

ghostbuster

Senior Member
http://s166.photobucket.com/albums/u91/ghostbuster7/?action=view&current=1174620635.pbw

Location:Medium size data processing centre

Problem:On the PDU's (power distribution units) all the ground current sensing circuits were in alarm.On each PDU(4 in total) the indicated ground currents ranged from 20-60 amps.

Facts:

1.Found spring loaded metal clips on the back side of the front cover panels making contact with either the hot or neutral screws on the receptacles.

2.Contact with the hot tripped the breaker.The installation crew would then rotate the offending cover plate by 180 degrees and re-install, then reset the breaker.These clips would no longer line up with the hot screws and these breakers would no longer trip.

3.The crew finished their install with the breakers no longer tripping.They left the site,their job was finished (they did not tell anyone about these "little minor electrical flashovers" that had occured).

4.The crew did not realize they were now causing neutral to ground dead shorts on most of these receptacles.This was the cause of this very high ground current on each power system.

5.The mfr. was contacted and admitted he had changed his welding jig set up for the positioning of these clips.

6.All new "proper" plates and replacement damaged receptacles were installed at this site.Equipment had to be turned off during re-install . Computer Downtime approx. 4 days required, +++ lots of extra manhours:)

7.The local inspection agency was also brought into the loop.
3.jpg


2.jpg


1-1.jpg
 

brian john

Senior Member
Location
Leesburg, VA
My Friday Post:

This is a 400 amp CB; I was called to a facility to check emergency a CB that had been closed into a fault resulting in an electrician receiving 2nd degree burns.

This is not the first time I have seen this issue. When a CB opens due to a fault or overcurrent, the source of the OC or fault MUST be investigated. Additionally the CB should be visually inspected (with the source of power removed) OPENED UP, or meggered and micro-ohmed/DLRO. Had the tech meggered this CB and feeder he would have gotten low resistance readings, had he visually inspected this he would have seen something close to this (obviously after the second opening the damage most likely was/is worse. The feeder was faulted.

Closing a CB or any OCP into a fault is CRAZY, WRONG, DANGEROUS and you are can be held liable for any damage the facility incurs.


CircuitBreakers.jpg
 