All the equipment here is new, recently energized service. Notice anything odd?

Lifeskillsservice.jpg
 

480sparky

Senior Member
Location
Iowegia
Serious lack of phase tape.

No lock on the CT cabinet.

What are the OH pipes for?

No grounding to meter.

Al and shovel missing.
600003434.gif
 
Last edited:

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Serious lack of phase tape.

Is there a requirement to phase the conductors in a CT cabinet?

No lock on the CT cabinet.
I took it off to open it.:roll:

What are the OH pipes for?
Bingo, POCO couldn't make up their mind, a few dollars worth of materials wasted sticking up through the roof.

No grounding to meter.
Meter base grounded as per POCO.

Al and shovel missing.
600003434.gif
Don't tempt me.

Load side EGC?

Conduits on the left come from POCO transformer.
 

rt66electric

Senior Member
Location
Oklahoma
where's waldo's electrode -

where's waldo's electrode -

Where is the funny looking block that is supposed to connect the white wire to the smaller green wire? not to mention the bare wire that goes to the copper stick pounded into the ground???
 

220/221

Senior Member
Location
AZ
Notice anything odd?

The whole thing looks odd to me.

Here, the POCO feed would be 4 wire (no egc) and there would be a disconnect there.

So....these feeders loop thru the CT can and they wrap the CT's around them uh? The disconnect is at the panel inside?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Where is the funny looking block that is supposed to connect the white wire to the smaller green wire? not to mention the bare wire that goes to the copper stick pounded into the ground???

Main bonding jumper and GES inside at MDP.

The whole thing looks odd to me.

Here, the POCO feed would be 4 wire (no egc) and there would be a disconnect there.

So....these feeders loop thru the CT can and they wrap the CT's around them uh? The disconnect is at the panel inside?

There is 4 wire coming from POCO but customer owned. These are the conduits on the left with no paint. The CT's are solid (300-5). A real wrestling match to pull to POCO transformer then get them through the CT's then pull into MDP. This is 2 sets of 500's. Al has a special shovel he uses to wrestle these conductors.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
I don't see any CT's there Bob.

I see, CT's bolt in between the lugs, that sweet.
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Looks like the CT cabinet is not grounded to the neutral conductor. And there is no need for the EGC's in with the conductors going to the main disconnect. Once the neutral is bonded to the CT cabinet they will become ea parallel path for the neutral current.
 

LLSolutions

Senior Member
Location
Long Island, NY
i would use migb's on the top conduits if they're metallic, bond it properly. On a new note, why does the meter enclosure look like Stainless? If required why not the ct cabinet also?
 