(Amd) 210.12 Arc-fault circuit-interrupter protection.
(Amd) (B) Dwelling unit bedrooms. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter, listed to provide protection of the entire branch circuit.
Exception 1: The location of the arc-fault circuit interrupter shall be permitted to be at other than the origination of the branch circuit in compliance with (a) and (b):
(a) The arc-fault circuit interrupter installed within 6 feet of the branch circuit overcurrent device as measured along the branch circuit conductors.
(b) The circuit conductors between the branch circuit overcurrent device and the arc-faullt circuit interrupter shall be installed in a metal raceway or a cable with a metallic sheath.
Exception 2: Smoke detectors shall be permitted to be supplied by branch circuits without such protection providing such branch circuits supply no other outlets within the dwelling unit bedroom.