Yes IMORiser is at a pole, with utility meter and main disconnect. Is a 4 wire required underground to the house?
IMO, Yes a 4-wire system is required based on 250.32(D) of 2008 edition. The service pedestal qualifies as a structure and any wiring from that point of main disocnnect becomes a feeder.
without the disconnect at the meter you could do this and bond the ground rods, equipment grounds and neutral together at the house. With the disconnect, be careful here: you will end up without a low impedance path back to the source. your equipment would be connected to dirt as required, but you would not clear faults.What if you run 2 hots 1 neutral and derive your ground from ground rods at the house?
If the disconnect at the meter has OCPD, then your bond should be there and a 4-wire would need to be run to the house.
Some say the meter location described is considered a structure & therefore the ECG should be inserted. I have had interpretations from code authors refering the meter location as electrical equipment and not a structure. The NEC 2014 addresses the meter ?METER DISCONNECT NOT SERVICE EQUIPMENT.? Kinda a tangled web.
Once you hit an overcurrent device they are no longer service conductors, they are feeders whether multiple structures comes into play or not.Who cares whether it is a structure or not? I dont see that that has anything to do with it. service conductors can be run along one structure to feed another. There is no requirement to turn them into a feeder as long as they dont pass thru the first structure.
Or, looking at it another way, if the disconnect is not associated with an overcurrent device, it is just a random POCO disconnect, but not a service disconnect.Once you hit an overcurrent device they are no longer service conductors, they are feeders whether multiple structures comes into play or not.
See definition of service conductors in article 100. It doesn't mention overcurrent devices but does mention service disconnect.
A service disconnect will have an overcurrent device associated with it, 230.91 tells us this.
A slight variation of this is the way meter pedestals were treated where I live. All of them have a 200A breaker in them but since the pedestal belonged to the POCO it was not considered the first disconnect.Or, looking at it another way, if the disconnect is not associated with an overcurrent device, it is just a random POCO disconnect, but not a service disconnect.
Fine with me. Curious though, what present or future disaster is it that you would be saving anybody in the house from with the fourth wire?The only way I would consider the Breaker inside a (Power Company provided) Pedestal Combo Meter Main "Not" the first means of disconnect, would be if the Power Company put their seal on the access cover to the Breaker.
Otherwise I feel a 4 wire feeder is required from that point on.
JAP.
I know very well the difference between sec and feeders. I interpreted the preceding post as implying a disconnect is required at a meter pedestal structure.
From the 2008 code (I think thats the cycle it changed) structure or not, you would need a 4 wire feeder after the service disconnect
If the meter and disconnect belong to the POCO the NEC would not apply to any of their equipment.
If the wires come from the POCO equipment that is not covered by the code wouldn?t the wires be service conductors.
90.2 Scope.
(B) Not Covered.
(5) Installations under the exclusive control of an electric utility where such installations
c. Are located in legally established easements or rights-of-way