Hi everyone,
Try to be concise as possible here. The client wishes to make use of the Fronius Symo 20.0-3 480 inverter. According to the installation manual, it is applicable on the following grids, that being the 480V WYE grid.

According to the electrician who I am creating the 3 line diagram for, he is suggesting that we go from the Inverter to a 480 Delta > 208 Y Transformer, then do a line side tap via a 208V fused disconnect. All was dandy until I did some investigation.
It looks like this inverter requires the Neutral. Therefore, how on earth can this possible work. the 480V Delta side of the transformer has nowhere to land a neutral, and the neutral that is on the 208Y of the transformer is already spoken for in the sense that it is going back to the neutral bar on the 208Y panel board.
Therefore, after scratching my head for awhile, I basically came up with 2 ideas..
a. This design is flawed, and it may need a new inverter selection
b. Use a 480Y to 208Y transformer which apparently is quite rare, but does exist.
Aside from option (a), am I correct in thinking this is an impossible design? Keep in mind that the inverter DOES require a neutral for voltage sensing.
Does anyone have experience with this inverter or this scenario in general? I emailed the electrician and let him know my thoughts, and that perhaps a different design was in order. But, maybe I jumped the gun and am simply not seeing the solution?
Please advise. Thanks.
Try to be concise as possible here. The client wishes to make use of the Fronius Symo 20.0-3 480 inverter. According to the installation manual, it is applicable on the following grids, that being the 480V WYE grid.

According to the electrician who I am creating the 3 line diagram for, he is suggesting that we go from the Inverter to a 480 Delta > 208 Y Transformer, then do a line side tap via a 208V fused disconnect. All was dandy until I did some investigation.
It looks like this inverter requires the Neutral. Therefore, how on earth can this possible work. the 480V Delta side of the transformer has nowhere to land a neutral, and the neutral that is on the 208Y of the transformer is already spoken for in the sense that it is going back to the neutral bar on the 208Y panel board.
Therefore, after scratching my head for awhile, I basically came up with 2 ideas..
a. This design is flawed, and it may need a new inverter selection
b. Use a 480Y to 208Y transformer which apparently is quite rare, but does exist.
Aside from option (a), am I correct in thinking this is an impossible design? Keep in mind that the inverter DOES require a neutral for voltage sensing.
Does anyone have experience with this inverter or this scenario in general? I emailed the electrician and let him know my thoughts, and that perhaps a different design was in order. But, maybe I jumped the gun and am simply not seeing the solution?
Please advise. Thanks.